RandallW wrote: ↑Thu Oct 24, 2024 5:03 amI understand the advantage of converting from 25Hz to 60Hz is the substation equipment is both less complex and more standard when the 60/25 Hz transition does not need to be made.
You can use standard 60hz equipment, so once converted the system would be simpler and not require the static converters and could be fed from anywhere.
Given that the only equipment in the NEC that requires 25Hz are the SEPTA Silverliner IVs and maybe some MOW equipment, once those are retired, there is no advantage to retaining 25Hz electrification anywhere on the NEC.
BUT, and it's always a big BUT, there are a lot of reasons why this would be a very complicated and expensive project:
1. While the Reading system is a traction power system only fed from one point, the PRR system is an entire power grid that essentially pre-dates any kind of widespread AC power grid in the area that originally generated all of it's own power. Thus, it has transformers, substations, and single-phase transmission lines all built specifically for the PRR system, and not for 60hz power.
2. There is other stuff, like signals and equipment at stations built to run on 25hz. Not a huge hurdle, but $$$.
3. There are two 25hz turbines at the Safe Harbor Dam that produce power for Amtrak natively at 25hz.
4. Amtrak upgraded the rotary converts to static converters, partly due to the cost of the 25hz system.
5. For electrification of passenger and freight operations, NEC locomotives are essentially bespoke anyway. Even with widespread electrification of freight railroads and long-distance passenger trains that use them, the national rail system is mostly standardized on I-ETMS, 16'2" overhead clearance, and would be using 25kV/60 for electrification. The NEC isn't just different because it uses 25hz, it also uses ACSES II, and has a clearance limit for 15'6" for freight and 14'6" with round corners at the North River Tunnels for passenger traffic, so both freight and passenger locomotives have to be somewhat bespoke for NEC use anyway.
6. There would be efficiency savings by not having to convert 60hz power to 25hz power, but due to clearances, it's likely that the NEC, like the New Haven Line to the north, would be converted to 12.5kV/60 not the now-standard 25kV/60, limiting the efficiency gains by utilizing a higher voltage in a 50kV split-phase system like Amtrak uses on the Shore Line.
7. The capital cost for a project that gains essentially nothing would be absolutely massive, and there are many, many other electrification projects waiting for funding that would be far more impactful than converting the 25hz system to 60hz. In addition, the NEC instead is in need of something like $30B in repairs and upgrades just to get to a state of good repair and maximize the track speed that's possible within the current physical alignment including bridge replacements and other speed restrictions.
So yes, there would be some weight savings by not having 25hz transformers but any weight differences and wear and tear is going to be far more driven by getting modern equipment that takes advantage of the new FRA crash standards and doesn't require them to be quite as extremely overbuilt as previous designs (including the now outdated M-9 design). It is even likely that an M-10 car under the new crash standards could work on 25hz power, although such a design would still be limited in use and different than an AC EMU used in through service, as third rail equipment doesn't work with low-level platforms, requiring a separate AC EMU design that can handle low-level platforms while the M-10 design would handle AC and third rail power instead.